    Default Wiring an electric kiln



    I have an old Gare kiln (60 amps) which I need to wire about 100 ft from the breaker switch. I am told by some I need 04 and by some I am told I need 4 guage wire. Are these numbers synonymous? (I am writing this for my husband who will do the wiring, so please feel free to correct my terminology so I can tell his correctly what he needs. Are guage and size the same things?

  2. #2
    ArnoldHoward is offline Junior Member User
    This user has no status.
     
    Join Date
    Jul 2009
    Posts
    8
    Classifieds
    0

    Default

    Quote Originally Posted by Mary Ellen View Post
    I have an old Gare kiln (60 amps) which I need to wire about 100 ft from the breaker switch. I am told by some I need 04 and by some I am told I need 4 guage wire. Are these numbers synonymous?
    The lower the number, the thicker the wire. #4 copper wire would be thick enough except that your circuit will be 100 feet long. Can you install your kiln closer to the breaker box? The longer the circuit, the greater the voltage drop. For a 100 foot circuit, I would probably choose #2 copper wire. (Never use aluminum wire.)

    Sincerely,

    Arnold Howard
    Paragon Industries, L.P., Mesquite, Texas USA
    ahoward@paragonweb.com / www.paragonweb.com


    Sincerely,

    Arnold Howard
    Paragon Industries, L.P., Mesquite, Texas USA
    ahoward@paragonweb.com / www.paragonweb.com